Leviton Level 2 Charger is a Phantom Power Drain


murphy62

Recommended Posts

I installed a Leviton level 2 plug-in charger in my garage in preparation for my Fusion Energi when it eventually is delivered. I measured the power it idles at and found that it is about 10 watts. Over a month that amounts to 7.3 kwh wasted. I modified the installation to have an on/off switch so it will only be turned on when needed. That's one less phantom power drain in my house.
:)

Link to comment
Share on other sites

I forgot to mention that the reason for the switch instead of just unplugging it is that a 6-20P plug takes a lot of force to remove and to connect. That got annoying after just two times of unplugging it. It is another solution if the force required doesn't bother you.

Link to comment
Share on other sites

I forgot to mention that the reason for the switch instead of just unplugging it is that a 6-20P plug takes a lot of force to remove and to connect. That got annoying after just two times of unplugging it. It is another solution if the force required doesn't bother you.

 

Hadn't thought about a switch for a 220V line with 2 hot legs - how did that work? Do they make 220V switches with 2 legs or did you have to rig something up?

Link to comment
Share on other sites

Hadn't thought about a switch for a 220V line with 2 hot legs - how did that work? Do they make 220V switches with 2 legs or did you have to rig something up?

A double pole switch is available at Lowe's.

 

http://www.lowes.com/pd_89198-334-CSB220W_0__?productId=3569190&Ntt=double%2Bpole%2Blight%2Bswitch&pl=1&currentURL=%3FNtt%3Ddouble%252Bpole%252Blight%252Bswitch&facetInfo=

 

The hard part is finding one rated for 20 amps. The vast majority of switches at Lowe's are 15 amp switches.

Edited by murphy62
Link to comment
Share on other sites

Never use a single pole device in a two pole 240V circuit. You're asking for someone who believes it's off 'cause the switch says so to be given a possibly fatal shock. Not up to code either.

That's true. I'll remove the single pole observation from my previous post.

 

However anyone who works on a circuit without turning off the breaker feeding the circuit is an accident waiting to happen.

Link to comment
Share on other sites

Fits in a normal box as you can see by the picture.

 

I guess I never paid attention to them since they look the same as the single pole switches.

It's less complicated internally than a 4-way switch that is used with two 3-way switches to provide control of a light from three locations.

Link to comment
Share on other sites

It's less complicated internally than a 4-way switch that is used with two 3-way switches to provide control of a light from three locations.

 

Good point. I actually bought 2 3-way switches and wired them up on the worktable and used a voltmeter to figure out how they worked. Now I can wire it up any way I need to - power in one switch, load out the other, power and load at the same switch, power at the fixture, etc. etc. Drove me crazy until I figured it out.

Link to comment
Share on other sites

  • 2 weeks later...
  • 3 weeks later...
A double pole switch is available at Lowe's.

 

http://www.lowes.com/pd_89198-334-CSB220W_0__?productId=3569190&Ntt=double%2Bpole%2Blight%2Bswitch&pl=1&currentURL=%3FNtt%3Ddouble%252Bpole%252Blight%252Bswitch&facetInfo=

 

The hard part is finding one rated for 20 amps. The vast majority of switches at Lowe's are 15 amp switches.

 

If you are using the Ford box (32Amp) then you will need a 40 amp switch. Another option is to install a small fuse-box type junction box with a dual 40amp breaker near the Charging station and just trip the breaker (like a switch).

 

Shutting/turning it off, you will lose the ability to check it or do a warm-up from your cell/iPad, right? I was told that the Ford Charger had some pre-programmed Ford code in it. Does anyone know if that is true?

Link to comment
Share on other sites

Why would the Ford box be the 32 amp version when the car is incapable of using more than 16 amps?

 

Looking to do my own install, I checked with the manufacture (Leviton), here is what they told me "the Ford unit is a 32A rated unit and will require a minimum of 8 Gauge wire. Since there will have to be a conduit from the breaker panel to your disconnect switch, I would recommend THHN wire in at least 8 Gauge. The breaker would have to be a double pole 40A and the outlet would be a NEMA 6-50R."

Link to comment
Share on other sites

Looking to do my own install, I checked with the manufacture (Leviton), here is what they told me "the Ford unit is a 32A rated unit and will require a minimum of 8 Gauge wire. Since there will have to be a conduit from the breaker panel to your disconnect switch, I would recommend THHN wire in at least 8 Gauge. The breaker would have to be a double pole 40A and the outlet would be a NEMA 6-50R."

If you have trouble finding a double pole 40A 240V breaker resist the urge to use a 50 A breaker. That would require the wire size to be increased to 6 gauge. Breakers are sized to protect the wire and a 50 amp breaker with 8 gauge wire is not allowed.

Link to comment
Share on other sites

If you have trouble finding a double pole 40A 240V breaker resist the urge to use a 50 A breaker. That would require the wire size to be increased to 6 gauge. Breakers are sized to protect the wire and a 50 amp breaker with 8 gauge wire is not allowed.

 

Actually I already did that part of the install. Found a 40 amp dual and used 6 gauge wire anyway. Hope to have the Charging Station in today. I'll post all about it once it is in.

Link to comment
Share on other sites

Mr. Electric came by and mounted my Charging Unit, now I just need the car. Actually, I need to clean the garage, fix-up and paint the walls, then I'm ready....but getting closer.
PS: anyone know how to display images smaller on a post then they are in the URL?

IMAGE_E2935D4A-1FD3-4877-AEB8-8CA8C43C82

Edited by taylorjd
Link to comment
Share on other sites

PS: anyone know how to display images smaller on a post then they are in the URL?

 

If you are using Windows, open your photo in Paint, then use the Resize tool (CTRL W) to reduce the size by, say 50% (or more).

 

Re-save it to your hard drive and upload it to the sharing site you are using (Google?). If you overwrite it with the same filename/location as the URL you used in your post above, it will modify that photo, too.

Link to comment
Share on other sites

If you are using Windows, open your photo in Paint, then use the Resize tool (CTRL W) to reduce the size by, say 50% (or more).

 

Re-save it to your hard drive and upload it to the sharing site you are using (Google?). If you overwrite it with the same filename/location as the URL you used in your post above, it will modify that photo, too.

 

I know how to resize the image, I just wanted to use like an <img> tag to display it smaller on the forum without have to create a second smaller, less resolution image. If idid, then I would want the smaller image to be clickable to a full image. But i do not see a way to add HTML tags like that in here.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...